NCARB PDD Practice Exam Question - Insulation Values

Comments

7 comments

  • Avatar
    rebekkak

    Hi Amber,

    Choice 1 is incorrect because the 1" of polystyrene rigid in the cavity is not enough to meet the code, which says that R-5 c.i. (continuous insul) is needed in the metal walls of a commercial building.  1" at R4.5 = R4.5.

    Choice 3 is the correct one!

    Hope this helps!

    Rebekka O'Melia, Registered Architect, NCARB, B. Arch, M. Ed, Step UP,  Step UP ARE 5.0 Courses

    0
    Comment actions Permalink
  • Avatar
    Amber Bonifacio

    Hi Rebekka thanks for your help. Passed PDD! On to my last exam PPD!

     

     

    0
    Comment actions Permalink
  • Avatar
    rebekkak

    You're welcome!  And congrats on passing Amber, that's great!!  You're almost done!

    Rebekka O'Melia, Registered Architect, NCARB, B. Arch, M. Ed, Step UP,  Step UP ARE 5.0 Courses

    0
    Comment actions Permalink
  • Avatar
    David Bowen

    I'm confused by this question as well. 

    The chart requires an R-value for 'Mass' walls (I am assuming this is the brick maybe I am wrong) of R7.6.

    I had been calculating the 1.5 inches of polystyrene rigid as insulation for that wall portion, which is 6.75 and less than the mass wall in the chart requires.

    Or is it that the brick is ignored and the 1.5 inches of polystyrene rigid is just extra above and beyond the steel frame wall with batts? 

    0
    Comment actions Permalink
  • Avatar
    rebekkak

    Brick veneer is not a mass wall.  It’s a veneer.  If it were 2-3 courses of brick or solid concrete, then that’s a mass wall.

    Rebekka O'Melia, Registered Architect, NCARB, B. Arch, M. Ed, Step UP,  Step UP ARE 5.0 Courses

    0
    Comment actions Permalink
  • Avatar
    lindamejia

    Can someone explain how to do this question and why option 3 is correct. I dont understand which is the code requirements. I got the values for each option but I’m unclear on what I’m comparing it to?

    0
    Comment actions Permalink
  • Avatar
    abruno168

    lindamejia

    The goal of this question is to utilize the code table for required insulation values and the information given in the scenario to tabulate the proposed assemblies and select the compliant one.

    The question tells us that the roof being used has insulation entirely above the deck for an office (nonresidential) application. The minimum R-value for this assembly is R-25 continuous insulation. The walls are steel-framed with a brick veneer, which requires R-13 and R-5 continuous insulation.

    The 3 options feature polyiso (R8/inch), polystyrene (R4.5/inch), fiberglass batts (R3.5/inch), and rock-wool (R3/inch) as the insulators in the assembly. Using these numbers, we have 4” polyiso (R32 CI) and 3” polyiso (R24 CI) for the proposed roof assemblies, which eliminates option 2 that does not comply with the requirements in the table (R25 CI).

    Moving to the continuous rigid insulation for the remaining two options, we have 1” (R4.5 CI) and 1.5” (R6.75 CI), which eliminates the first option due to the table requirement (R5 CI). Finally, the 4.5" rock wool (R13.5) is compliant with the required minimum R-value for steel-framed walls above grade, making option 3 the correct option.

    1
    Comment actions Permalink