NCARB PDD Practice Exam Question - Insulation Values

Comments

5 comments

  • Avatar
    Rebekka O'Melia

    Hi Amber,

    Choice 1 is incorrect because the 1" of polystyrene rigid in the cavity is not enough to meet the code, which says that R-5 c.i. (continuous insul) is needed in the metal walls of a commercial building.  1" at R4.5 = R4.5.

    Choice 3 is the correct one!

    Hope this helps!

    Rebekka O'Melia, Registered Architect, NCARB, B. Arch, M. Ed, Step UP,  Step UP ARE 5.0 Courses

    0
    Comment actions Permalink
  • Avatar
    Amber Bonifacio

    Hi Rebekka thanks for your help. Passed PDD! On to my last exam PPD!

     

     

    0
    Comment actions Permalink
  • Avatar
    Rebekka O'Melia

    You're welcome!  And congrats on passing Amber, that's great!!  You're almost done!

    Rebekka O'Melia, Registered Architect, NCARB, B. Arch, M. Ed, Step UP,  Step UP ARE 5.0 Courses

    0
    Comment actions Permalink
  • Avatar
    David Bowen

    I'm confused by this question as well. 

    The chart requires an R-value for 'Mass' walls (I am assuming this is the brick maybe I am wrong) of R7.6.

    I had been calculating the 1.5 inches of polystyrene rigid as insulation for that wall portion, which is 6.75 and less than the mass wall in the chart requires.

    Or is it that the brick is ignored and the 1.5 inches of polystyrene rigid is just extra above and beyond the steel frame wall with batts? 

    0
    Comment actions Permalink
  • Avatar
    Rebekka O'Melia

    Brick veneer is not a mass wall.  It’s a veneer.  If it were 2-3 courses of brick or solid concrete, then that’s a mass wall.

    Rebekka O'Melia, Registered Architect, NCARB, B. Arch, M. Ed, Step UP,  Step UP ARE 5.0 Courses