Control joints (CJ) for a CMU wall
An architect is working with a structural engineer to layout the control joints (CJ) for a CMU wall. They successfully layout all the CJ according to the CMU block module. Which of the following cannot be a CJ-to-CJ dimension in this wall’s CJ layout? Why?
- 21’-4”
- 20’-8”
- 19’-8”
- 22’-0”
Gang Chen, Author, AIA, LEED AP BD+C (GreenExamEducation.com)
-
The answer is c. 19’-8” because it is not set up per CMU block module and will require the cutting of CMU blocks and cost more money. The trick to set up the CJ-to-CJ dimension is if the feet is an odd number, then the inch must be 4”, such as 3’-4”, 15’-4”, etc. If the feet is an even number, then the inch much be 0” or 8”, such as 8’-0”, 12’-8”, etc.
Gang Chen, Author, AIA, LEED AP BD+C (GreenExamEducation.com)