How to size roof drains and scuppers?

Comments

4 comments

  • Avatar
    aagangchen (Edited )
    1. The minimum scupper size is 4”high x 16” wide
    2. If you want to consider block module, you can use 8”x16” size for a scupper in a CMU wall.
    1
    Comment actions Permalink
  • Avatar
    aagangchen (Edited )

    You are welcome. When I was young, I was hoping someone would guide me through the career path and ARE exams. That is what I am doing now to help younger professionals to have an easy path in their career.

    Gang Chen, Author, AIA, LEED AP BD+C (GreenExamEducation.com)

    2
    Comment actions Permalink
  • Avatar
    Todd

    Hi Mr. Chen, 

    To size for storm roof draining, do you multiple the following to get to table 1106.2:

    rate of rainfall X area of roof X 0.0104 (constant to get GPM) = GPM

     

    Thank you, 

    Todd 

    0
    Comment actions Permalink
  • Avatar
    aagangchen (Edited )

    Yes. Under the UPC/CPC storm drainage sizing method, the flow rate is typically calculated as:

    Q=I×A×0.0104

    Where:

    • Q = flow rate (gpm)
    • I = rainfall intensity (inches/hour)
    • A = horizontal projected roof area (square feet)
    • 0.0104 = conversion factor to convert (in/hr × sf) into gpm

    Example

    Roof area = 20,000 sf

    Rainfall rate = 4 in/hr

    Q=4×20,000×0.0104
    Q =832gpm

    You would then use Table 1106.2 (or applicable storm drain sizing table in your adopted code) to size the roof drains, leaders, and piping based on the calculated 832 gpm and pipe slope.

    Gang Chen, Author, AIA, LEED AP BD+C (GreenExamEducation.com)

    0
    Comment actions Permalink