Fire-resistance footnote

Comments

2 comments

  • Avatar
    Benjamin Sullivan

    The question includes "the roof is 35 feet from the highest level of seating."

    The exception in the footnote allows roofs to have 0 hr rating if the roof is at least 20 feet above any floor immediately below, & as long as the occupancies are not Groups F-1, H, M, and S-1.

    The exception applies to all occupancies except for Groups F-1, H, M, and S-1. So for Occupancy A, this exception can be used. If the space in the question was a Factory, Hazardous, Mercantile, or Storage occupancy, it would need a higher fire rating based on the probability that there are some flammable items being stored on the level under the roof.

    0
    Comment actions Permalink
  • Avatar
    Lila Guizado

    Thank you, Benjamin. 

    The way the footnote is written is quite confusing. I read it as only for those occupancy groups.

    0
    Comment actions Permalink