Fire-resistance footnote
Could someone please explain what I am missing on this NCARB practice exam question.
B footnotes is an exception for group F-1, H, M and S-1. If this is for a theater, which is group A, wouldn't this footnote not apply?
-
The question includes "the roof is 35 feet from the highest level of seating."
The exception in the footnote allows roofs to have 0 hr rating if the roof is at least 20 feet above any floor immediately below, & as long as the occupancies are not Groups F-1, H, M, and S-1.
The exception applies to all occupancies except for Groups F-1, H, M, and S-1. So for Occupancy A, this exception can be used. If the space in the question was a Factory, Hazardous, Mercantile, or Storage occupancy, it would need a higher fire rating based on the probability that there are some flammable items being stored on the level under the roof.