IBC stair width vs ADA stair width
For over 50 occupants, IBC states that the minimum stair width is 44".
Is there something in the ADA that states the minimum stair width is 48" though?
-
I believe the 48" ADA clearance is for the area of refuge.
https://images.app.goo.gl/F956NLKMysJxntPc6
-
Hi Frank,
I did not see the required minimum width in the 2010 ADAS or ANSI A117.1. However, it is mentioned in the IBC. For a Stairway to be considered as an accessible means of egress, the stairway shall have a clear width of 48" minimum between handrails (IBC 1009.3.2).
Also, I want to add to this point:
- "IBC states that the minimum stair width is 44"."
This is true but not always the case. The stair width sizing should be determined first as specified in 1005.3.1: The capacity, in inches, of means of egress stairways, shall be calculated by multiplying the occupant load served by such stairways by a means of egress capacity factor of 0.3 inch per occupant.
For example, if the stairway serves an occupant load of 155, then 155 x 0.3 = 46.5 inches. Now your minimum is 46.5", not 44".
Please sign in to leave a comment.
Comments
2 comments