Building Area Frontage Question

Answered

Comments

2 comments

  • Avatar
    Stephen Starks

    Janice,

     

    Refer to the definition given in code for "Sa":

    My understanding is that you can have a higher building, up to 6 stories for your building type / method of fire protection, but the number of stories for the allowable area calc. can only use 4 of those.

    The definition for 'Sa" states; "Use actual number of building stories above grade plane, not to exceed four", so you can only count 4 of those 6 allowable stories (taken from table 504.4) for use in the calculation.

    As to building area increase due to frontage, that is a separate value "If", and is calculated in one of two ways (refer IBC 2015, 506.3.1, and 506.3.3). The main factors for this value are the widths of the public rights of way, and the lengths of the perimeter walls that face those rights of way (detailed definitions / calculations are in these sections, so you should look at those if you have questions).

    Hope this helps.

  • Avatar
    Janice Chiu

    Thank you for taking the time to answer my question. It's clear now! :)