Mock ARE quesiton - Roof Fire Rating
Isn't the Exception b is only for F-1,H, M & S-1? The question is talking about a theatre with two level of seating levels (Group A definitely) but the correct answer is 0 hour of fire-rating. Someone please explain if you know something about this.
-
Thanks for the comment!
If you are talking about Exception b, for a roof structure above 20 feet, roof fire-rating is not required = 0 hours, I didn't miss it. The screenshot is too small, but that used exception NCARB have only works with the listed Groups I mentioned above, not to group A.
However, I checked the Table 601 on IBC did mention Group A, see snipshot below..
Please sign in to leave a comment.